Customer Support 7 days a week

Welcome Guest! You can not login or register.

Notification

Icon
Error

2 Pages<12
Options
Go to last post Go to first unread
denman  
#11 Posted : Wednesday, November 25, 2015 2:03:18 AM(UTC)
denman

Rank: Advanced Member

Groups: Senior Expert
Joined: 2/29/2008(UTC)
Posts: 19,638

Thanks: 1 times
Was thanked: 11 time(s) in 11 post(s)
I would leave it at 40.
If you ever replace the unit you probably would then have to have 40 amp breakers for the majority of units out there.
Also since the unit will draw 30 amps you want to have some leeway.

Note the above also depends on the wire gauge going to the unit.
A 40 amp breaker should have 8 gauge copper or 6 gauge aluminum.

I would also use some anti oxidant compound on the aluminum wire connections.
THIS FORUM IS DEAD!!!!!!!
Users browsing this topic
Guest (2)
2 Pages<12
Forum Jump  
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.