i have a trane xe80 furnace about 13 years old.
air conditioner installed about 8 years ago.
programmable thermostat - also 13 years old
Everything works good
EXCEPT.
when i turn the thermostat to 'ON' from auto nothing happens. (i.e. the fan does not run)

i want to leave the fan on all the time to circulate the air.

at one time the fan "on" worked, and it also worked after i had the AC installed as well.

perhaps the thermostat is shot.

any pointers on testing this. i have some electrical skills and understand most principles and know how to use a volt meter and that it is not a good idea to stick a knife into an electrical socket.
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
officework13  
#2 Posted : Tuesday, March 11, 2014 12:59:07 PM(UTC)
officework13

Rank: Member

Groups: Registered
Joined: 3/15/2011(UTC)
Posts: 14

see attached picture
OK, so i looked at the wiring and think i know what is likely wrong.
4 wires go to the thermostat.
Red to R
Green to G
Purple to Y
Black to W

with thermostat on auto i have 24 Vac from red on thermostat to each of the 3 wires, turn thermostat from Auto to on and voltages to green drop to near zero.

checked out furnace wiring.
there are 3 sets of wires as follows
Wire 1 - to thermostat
Red to R, Black to W, Purple to Y, Green - taped off (not used).

Wire 2 - to air conditioner
Black to Y, Red to C

Wire 3 - to exhaust fan
Black to R, Red to G

So how this is set up from my understanding is that the fan kicks in when we turn on the exhaust fan.

However, i want to be able to turn on the blower fan without turning on the exhaust fan. in winter i am loosing heat by doing this, and in summer i am loosing cool air.

my question, can i hook up the green wire (from the thermostat) to the circuit board (G) so i can use the thermostat to run the blower without turning on the exhaust fan.
officework13 attached the following image(s):
IMG_1567-details copy.jpg
Users browsing this topic
Guest (2)
Forum Jump  
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.