Am installing a comfort aire 75000 btu high efficiency gas furnace installed in the horizontal position Installation is complete and done according to manual and codes. Used 2" exhaust and intake with minimal elbows and length. Have 2 10" returns and 5- 6" supply. the problem is that the rollout and limits keep opening after a short period I have tried speeding up the fan, checked all ductwork for flow. The flame in the burner compartment seems to be large, erratic, and close to the limit switches. This is a new gas service and I have not yet verified the gas pressure, that will be my next step.
Any other suggestions would be greatly appreciated.
LCN
|
|
|
|
Rank: Member
Groups: Registered
Joined: 7/18/2009(UTC) Posts: 3
|
ck all your sizings, 75,000 btu requires more than what i see here
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/3/2009(UTC) Posts: 30
|
is this natural or lp gas? do you have the correct jet installed? also five 6" ducts can only move about 560 cfm and that isn't nearly enough air flow. most likely your problem. why do you have two 10" returns and only 5-6inch ducts? is this ten inch duct or ten inch grills?
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/18/2009(UTC) Posts: 3
|
Originally Posted by: lcn96 Am installing a comfort aire 75000 btu high efficiency gas furnace installed in the horizontal position Installation is complete and done according to manual and codes. Used 2" exhaust and intake with minimal elbows and length. Have 2 10" returns and 5- 6" supply. the problem is that the rollout and limits keep opening after a short period I have tried speeding up the fan, checked all ductwork for flow. The flame in the burner compartment seems to be large, erratic, and close to the limit switches. This is a new gas service and I have not yet verified the gas pressure, that will be my next step.
Any other suggestions would be greatly appreciated.
LCN Well. A 75000 Btu gas furnace is more than likely equipped with a 3 ton a/c blower which requires 1200 CFM. 5- 6" Supplies and 2-10" returns will only handle around 800 (just a guess) Also 75000 btu should be vented with a minimum 3" exhaust. Sounds to me like you have too much furnace and not enough duct.
|
|
|
|
Rank: Member
Groups: Registered
Joined: 11/18/2009(UTC) Posts: 3
|
Originally Posted by: lenbernhardt Well. A 75000 Btu gas furnace is more than likely equipped with a 3 ton a/c blower which requires 1200 CFM. 5- 6" Supplies and 2-10" returns will only handle around 800 (just a guess) Also 75000 btu should be vented with a minimum 3" exhaust. Sounds to me like you have too much furnace and not enough duct. First thing I would do is remove the exhaust vent pipe and watch your flame.
|
|
|
|
Forum Jump
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.
Important Information:
The AppliancePartsPros.com uses cookies. By continuing to browse this site, you are agreeing to our use of cookies.
More Details
Close