Customer Support 7 days a week

Welcome Guest! You can not login or register.

Notification

Icon
Error

Options
Go to last post Go to first unread
whsydddy9  
#1 Posted : Tuesday, October 26, 2010 2:40:48 PM(UTC)
whsydddy9

Rank: Member

Groups: Registered
Joined: 10/18/2010(UTC)
Posts: 41

The thermostat calls for heat, the furnace lights but when the fan switch should start the blower, the furnace hi-temps (shuts the gas valve off) then the blower starts after about 2 1/2 minutes. Soon the gas valve relights the burners and all runs well...What should I be looking for?

Thank you!
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
whsydddy9  
#2 Posted : Wednesday, October 27, 2010 4:16:53 PM(UTC)
whsydddy9

Rank: Member

Groups: Registered
Joined: 10/18/2010(UTC)
Posts: 41

I replaced the Camstat with a fan switch w/ safety...works fine now!:eek:
Users browsing this topic
Guest (2)
Forum Jump  
You can post new topics in this forum.
You can reply to topics in this forum.
You can delete your posts in this forum.
You can edit your posts in this forum.
You cannot create polls in this forum.
You can vote in polls in this forum.