fuchs1bl  
#1 Posted : Saturday, October 4, 2008 4:07:10 PM(UTC)
fuchs1bl

Rank: Member

Groups: Registered
Joined: 10/4/2008(UTC)
Posts: 3

RUUD Silohette II Furnace
Tappan Condensor Unit- Model FS3BA-024KA (2 Ton)

Here is my current issue.
Bought this home 18 months ago
Newer furnace and condesor unit.

During the winter, Furnace can warm the house very quickly and efficently with a large amount of air moving thru the registers. During the summer months when we run the AC, it struggles to cool the house at all, with very little air flow from the registers.

I asked a buddy, he had me check to make sure the wiring had both Furnace and AC wires on the high speed for the blower and when i checked they were. Any suggestions on how to alliviate the problem with little air flow while using the condenser during our summer?

Brian

Need more info, ask, Im new to this forum, and not very versed in HVAC
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
icehouse  
#2 Posted : Monday, October 6, 2008 4:59:05 AM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

The A/C should be wired for high speed, and the furnace should be wired low speed. If this does not help you need a fan control center. :)
fuchs1bl  
#3 Posted : Monday, October 6, 2008 2:43:17 PM(UTC)
fuchs1bl

Rank: Member

Groups: Registered
Joined: 10/4/2008(UTC)
Posts: 3

So if the AC is currently wired on high, i take it i need a blower control?
icehouse  
#4 Posted : Monday, October 6, 2008 3:52:57 PM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

No. Wire the A/C to high and furnace to low. If problem still exists change Amazon.com: Honeywell 90-113 Fan Control Center R8239A1052 Relay: Home Improvement :)
icehouse  
#5 Posted : Tuesday, October 7, 2008 3:30:34 AM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

Here is the wiring information. :)

http://customer.honeywel...pdf/60-0000s/60-0583.pdf
SublimeMasterJW  
#6 Posted : Wednesday, October 8, 2008 7:32:45 PM(UTC)
SublimeMasterJW

Rank: Advanced Member

Groups: Senior Expert
Joined: 5/6/2008(UTC)
Posts: 724

Was thanked: 1 time(s) in 1 post(s)
You should have a fan relay on the unit mounted on top of the fan center. The low speed is red and high is black . Common is usually purple or white. I would venture to say the wires are reversed on that fan relay.A dang Ruud ain't that complicated.
icehouse  
#7 Posted : Thursday, October 9, 2008 7:18:59 AM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

Originally Posted by: SublimeMasterJW Go to Quoted Post
You should have a fan relay on the unit mounted on top of the fan center. The low speed is red and high is black . Common is usually purple or white. I would venture to say the wires are reversed on that fan relay.A dang Ruud ain't that complicated.
To you and I no, to a DIYer yes. :)
fuchs1bl  
#8 Posted : Thursday, October 9, 2008 3:24:05 PM(UTC)
fuchs1bl

Rank: Member

Groups: Registered
Joined: 10/4/2008(UTC)
Posts: 3

Originally Posted by: icehouse Go to Quoted Post
To you and I no, to a DIYer yes. :)


Yes to me, but wiring is no problem for me, ill look into it.
"NO SWEAT" HEAT & AIR INC  
#9 Posted : Wednesday, October 22, 2008 10:19:40 AM(UTC)
"NO SWEAT" HEAT & AIR INC

Rank: Member

Groups: Registered
Joined: 10/22/2008(UTC)
Posts: 1

In my experience this problem is most likely the low voltage transformer located primarily in the furnace. when the transformer is shorted the fan relay will close on hgh speed and will provide heating when called for by the thermostat but will never provide the 24 volts necesary to change the furnaces motor speed or energize the contactor for the condensing unit, thus no cooling.
icehouse  
#10 Posted : Wednesday, October 22, 2008 5:27:40 PM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

Question ? How can the fan relay energize if the transformer is shorted ?