Hi, i own an international comfort products AC system (duct free systems)
The evaporator his always freezing. I tought the calibrated orifice might be clogg (chunk of welding). I need your help to know exactly where it should be located.

thank you
Sponsor
See inside of your appliance - diagrams and part photos for virtually every model.

powered by AppliancePartsPros.com
 
icehouse  
#2 Posted : Sunday, May 31, 2009 5:49:11 PM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

You are probably running the unit at a low outdoor temperature. This will prevent the condenser from condensing properly. As a result the refrigerant is pooling up in the condenser and starving the evaporator which results in lower pressure. Lower pressure results in lower temperature hence the coil freeze up. :)
patvac  
#3 Posted : Sunday, May 31, 2009 6:58:31 PM(UTC)
patvac

Rank: Member

Groups: Registered
Joined: 5/24/2009(UTC)
Posts: 3

We have discuss togetter already, but it's also freezing when it's really hot outside
icehouse  
#4 Posted : Monday, June 1, 2009 7:44:51 AM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

That was on another forum. Please list all conditions such as evaporator coil (clean thoroughly), condenser coil (clean thoroughly) filters changed, supply air temperature, return air temperature, dry bulb temperature, wet bulb temperature. Since this is a fixed orifice the charge is verified by super-heat, so post that reading as well. :)
icehouse  
#5 Posted : Monday, June 1, 2009 8:25:12 AM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

Use the following:
File Attachment(s):
Superheat charging curves for technicians.doc (93kb) downloaded 14 time(s).
patvac  
#6 Posted : Friday, June 5, 2009 12:21:28 PM(UTC)
patvac

Rank: Member

Groups: Registered
Joined: 5/24/2009(UTC)
Posts: 3

outside temperature 90 F with 20 % humidity

high Low
165 40
150 25
150 23 (psi)


Temperature external of evaporator 49.5F at 23 psi (shoud be -2F)
Temperature external of condenser 97 F at the fan at 150 psi (shoud be -82.5F)

Fitting at the condenser are full of ice and evaporator his starting to fill up too.

Thank you
icehouse  
#7 Posted : Friday, June 5, 2009 12:33:52 PM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440

Pressures are way off for R22. Head Pressure should be around 275# (110*F condensing temperature).
Suction 68# (40*F evaporator temperature)
icehouse  
#8 Posted : Friday, June 5, 2009 12:36:06 PM(UTC)
icehouse

Rank: Advanced Member

Groups: Senior Expert
Joined: 9/1/2008(UTC)
Posts: 440